Jennifer, I'm not an expert on the health effects of closed cell foam. A lot of people live in houses with closed cell foam and have no health problems from it, at least not short-term, acute problems. I do know of one person who had it removed from her crawl space because she was convinced it caused her dog to get sick, but I know only what she told me.  
I used this for the rim-joist in our home. A couple things: I put 1in solid core foam (cut to size) in each bay before using the spray foam. I also was able to do a relatively 'thick' spray to close off any potential gaps that may have existed. I turned off the HVAC and turned on some fans in the windows to exhaust out the fumes, and wore a mask (3m respirator).
Roof coatings made with acrylics, urethanes or asphalt soften under the stress of ponding water or snowpack. Eventually, these roof coatings will bubble and peel away from the substrate, leaving your roof vulnerable to leaks, rot, and decay. However, GacoRoof’s 100% silicone formulation is designed to stand up to whatever the elements dish out. Silicone will withstand areas of ponding water without softening, bubbling or peeling from the substrate. Acrylic, urethane and asphalt roof coatings decompose and wear away from the stress of harsh sunlight, UV rays, and freeze-thaw cycles.
When looking for a long-term roof solution, compare apples to apples. Liquid EPDM Rubber is a one-coat application. There are no primers needed, and when you begin adding up the cost of other systems that require primers and multiple coats, you are often exceeding the cost of liquid EPDM Rubber and have an inferior sealant on your roof. Why add unnecessary weight to a roof by using multiple-coat systems? Cut your time and labor costs in half with a one-coat system. Liquid EPDM has a very thick honey-like consistency and a slow cure time. One of the biggest benefits of the product. During the cure process, you will see bubbles resembling those created when you cook a pancake. This is the catalyst at work forcing the trapped air to the surface. What you have after the cure is a chemical bond between your roof and the coating. No other coatings produces this result. Other products trap this air making future cracks inevitable as temperatures change or expansion and contraction of the roof occur. http://m.youtube.com/watch?v=ggLAUsiuI_o
The Canadian National Building Code references the CAN/ULC S705.2 National Application Standard which must be followed during all installations of 2lb medium density closed cell polyurethane foam. Every installer of CAN/ULC-S705.1 compliant medium density, spray applied foam must be licensed in order to spray foam and hold valid photo ID issued by their Quality Assurance Program (QAP) provider showing their license is in good standing.

How Much Is Spray Foam


A: The RV roof coating works by waterproofing, weatherproofing and sealing our RV roofs from elements, including rain, snow, wind and other outer forces. It can also resist impact from leaves, twigs, dusts and other things that would otherwise damage the roof. It also works by reflecting UV rays, keeping the roof from degradation. The roof coating can also prevent leaks, heating and cooling loss and discomfort in our RV.

Empire Spray Foam is conveniently located in North Texas and proudly serves the Tarrant, Dallas, Denton, Wise, Parker, Hood, Johnson, Ellis, Kaufman, Rockwall, and Collin Counties with high quality spray foam and coatings designed to meet the needs of homeowners and businesses. Whether you are looking for energy savings, structural reinforcement, or weatherproofing, we have the solution. Call today to discuss your spray polyurethane foam options 817-516-2014.
One of the best ways to achieve it is to use the Heng’s rubber coating that can protect it from the elements, including sleet, wind, rain, and snow and UV rays. The product also does well in keeping our roof protected from dirt, leaves and twigs. With such protection received, our roof won’t degrade and we prevent ruining our recreational vehicle investment.
Check with the coating manufacturer who may be able to suggest applicators who have used their products and have familiarity with the application. Another option would be to interview contractors and ask specific questions about their proven ability to install roof coatings. Contractors affiliated with the National Roofing Contractors Association (NRCA) or local roofing contractor trade associations typically are more knowledgeable. Consult those groups’ websites for contractors. https://www.youtube.com/watch?v=ggLAUsiuI_o&hc_location=ufi
Empire Spray Foam is conveniently located in North Texas and proudly serves the Tarrant, Dallas, Denton, Wise, Parker, Hood, Johnson, Ellis, Kaufman, Rockwall, and Collin Counties with high quality spray foam and coatings designed to meet the needs of homeowners and businesses. Whether you are looking for energy savings, structural reinforcement, or weatherproofing, we have the solution. Call today to discuss your spray polyurethane foam options 817-516-2014.
Clean and free the roof surface of any debris and then dry the surface using a cloth. If you happen to have a current coating on the surface, check for adhesion. Consider removing loose coating, repairing, cleaning and then checking the area. Remember to use Energy Guard without thinning it because it is sold ready for use. Containers should not be left open except for a short period of time. You must also ensure that you check for any existing coating adhesion before opening Energy Guard. For application, you will require a brush preferably a bristle brush (synthetic) or a short nap roller. You can also use a good airless sprayer with a 0.031 or 0.027 tip to apply the coatings at (3000 psi/1gpm). You will also need water for cleaning up when you are done.
Heat which is created elsewhere that is transported by means of a fluid, such as water or in our case air. Spray foam insulation's most important attribute is the ability to air seal creating a custom airtight envelope within the building structure. The added benefit to air sealing is the ability to block convective heat transfer from interior to exterior during heating months and vice versa during cooling months, as the heat cannot escape through gaps in the buildings envelope without the aid of air movement from infiltration as a means of transport.
Simple – we’ve seen experienced contractors work with the separate nitrogen tanks and spray foam rigs and have one heck of a time. These spray foam insulation kits are quick to learn and simple to use. They’re designed to be easy so you get results the very first time you spray. Thorough Instructions, 24/7 Product Support, and videos make it easy to install.

Spray Foam Cost


Thank you, Allison. We have a split system unit (actually 5) with the heat being propane. The foam guy said that it needed ventilation, so completely sealing the attic wouldn't be a good idea. It sounds like you are saying that the systems need to be vented out of the attic or replaced with some type of closed system. But I shouldn't bother spraying if the plan is to leave the soffet vents open. Is that correct? https://www.youtube.com/watch?feature=youtube.be&v=ggLAUsiuI_o

“It’s been scientifically proven that the temp of the shingles rises only a couple of degrees when there is an unvented attic compared to a vented attic,” said Garry Barlow, estimator at RetroFoam of Michigan. “If we lived in a southern state it has been proven that the longevity of the shingle did diminish by only one year. In the northern states there was no difference in the life span of the shingles.”
I don't know if it's common or uncommon, but installing a layer of rigid foam above your roof sheathing in order to interrupt thermal bridging is always a good idea, and is preferable in all respects to a roof assembly without any rigid foam above the sheathing. If you decide to install rigid foam above the roof sheathing, you shouldn't use closed-cell spray foam under the sheathing; either use open-cell spray foam (which is vapor-permeable) or a fluffy insulation like cellulose, mineral wool, or fiberglass (any of which will allow the roof sheathing to dry to the interior).
Clean and free the roof surface of any debris and then dry the surface using a cloth. If you happen to have a current coating on the surface, check for adhesion. Consider removing loose coating, repairing, cleaning and then checking the area. Remember to use Energy Guard without thinning it because it is sold ready for use. Containers should not be left open except for a short period of time. You must also ensure that you check for any existing coating adhesion before opening Energy Guard. For application, you will require a brush preferably a bristle brush (synthetic) or a short nap roller. You can also use a good airless sprayer with a 0.031 or 0.027 tip to apply the coatings at (3000 psi/1gpm). You will also need water for cleaning up when you are done. 

How Much To Charge For Spray Foam Insulation


It works 100% as an EPDM rubber coating while also boasting of up to 5-year warranty. Another advantage of this liquid coating is its wide coverage. It comes in a 1-gallon kit, which is capable of covering an area of around 42 to 45 square feet. In addition, it is capable of withstanding a wide range of temperatures – from 6o degrees to 300 degrees Fahrenheit.

Spray Foam Polyurethane


You can also take advantage of Heng’s rubber roof coating if you need to coat your RV’s rubber roof. It works well in sealing EPDM rubber roofs. It is also useful on seams and tears as well as in sealing vents and air conditioning units. This roof coating is a good choice if you are just in search of that with a 1-gallon capacity at the most reasonable price. 

Spray Foam Exterior Walls


Also, I'm wondering... Is this website is being regularly updated? A local installer (in Oct, 2010) in MA quoted over twice the price you list here. "Open cell alone ~$1.35 per sq ft for R-13. Or a 'hybrid method' using 2inch closed cell for R-13 followed by 1.5inch open cell for R-6. Hybrid is $2.85 per sq foot for R-19 rating". Maybe installers are charging higher prices to profit from those trying to meet government energy rebate by Dec 31?
Open-cell is also known as half-pound foam. It has an R-Value of 3.5-3.6 per inch, and its density is bout 0.5 pounds per cubic food. Low-density foams like these are made partially from raw biological materials Carbon dioxide or water is also used in the makeup. Open-cell uses far less material than closed-cell, but its R-Value is lower. Also, open cell requires a vapor retarder (like gypsum wallboard) and is riskier when used for roof sheathing. It's not highly recommended that you use open-cell insulation if you live in a cold climate unless you have that extra barrier. You should also compare how much money you spend versus how effective the open-cell insulation is wherever it's installed.

Spray Foam Existing Wall


That’s $58.3 Billion dollars. That’s roughly how much money we wasted in 2010 in the US according to the Department of Energy because of air leaking out of our building envelopes. If your building leaks energy, you’re paying more for energy than you need to. Clearly you’re not alone. If you’re ready to claim your share of the savings, it’s quicker and easier than you think.
If you’re not familiar, spray foam is a type of insulation that expands after you spray. The foam expands and seals, avoiding any type of unnecessary moisture (which can create mold) or encouraging pests to eat through your walls. It protects the lining of your house, and even can protect the heating and cooling of your house during those unbearably cold or hot days.
Superior sealant: Spray insulation foam penetrates all of the spaces where it's applied, including in wall and ceiling cavities and around joists, joints, and beams. The airtight seal created by insulation foam is impervious to the elements and provides added benefits such as keeping pests out, improving indoor air quality, and blocking outdoor noise.
If you haven’t considered spray foam insulation, now may be the time to start looking into it. As you know, having proper insulation will help reduce your heat and air conditioning bills. In specific, spray foam insulation can be particularly helpful during renovations. It can provide a barrier between outside walls, and even a sound barrier for the inside.
R-value, the thermal resistance measure of insulation, varies between all insulation products whether they are fiberglass, cellulose, open-cell spray foam insulation or closed-cell sprayed-in foam insulation. Generally speaking the rule of thumb is the higher the R-value, the greater the insulating power.  Focusing on spray foam insulation materials, there is a difference between the two main types. According to industry publication, Fine Home Building, the R-value for open-cell spray foam is between R-3.5 – R-3.6 per inch. However, there are open-cell spray foam insulation products actually offer R-3.7 per inch such as Icynene Classic and Icynene Classic Max. The open cell structure of low density foam insulation means the R-value is lower than its closed-cell counterpart. Nevertheless, open-cell spray foam does offer superior and consistent thermal insulation and air sealing properties. https://www.youtube.com/e/ggLAUsiuI_o
One of the best ways to achieve it is to use the Heng’s rubber coating that can protect it from the elements, including sleet, wind, rain, and snow and UV rays. The product also does well in keeping our roof protected from dirt, leaves and twigs. With such protection received, our roof won’t degrade and we prevent ruining our recreational vehicle investment.

Stop making the same repairs using less reliable products that are not EPDM based, are not UV and ozone resistant, and do not have flexibility built into the material (causing them to crack). EPDM rubber will expand and contract with any surface as seasons change, and will not crack as a result of temperature changes. Other products will begin to bubble and crack in less than two years.


Silicone based coatings can be spray or roller-applied, and should utilize a medium-nap roller when rolled. These coatings are applied anywhere from 2 to 3.5 gallons per 100 square feet, depending on the substrate. Silicone has two major advantages over the other four types of coatings that should be considered when searching for the best roof coating: 1) it can resist ponding water for extended periods of time and 2) it can adhere to most substrates without a primer. Because of these two major advantages, silicone is the best roof coating that satisfies both quality and cost-effectiveness.
Henry 587 Dura-Brite White Elastomeric Roof Coating is Henry 587 Dura-Brite White Elastomeric Roof Coating is a premium high solids formula offering better weather protection solar reflectivity and longevity than economy grade reflective roof coatings. Cured coating forms a permeable membrane which prevents liquid infiltration but allows moisture vapor to vent or breathe out of underlying substrate. Recommended ...  More + Product Details Close
It also has a great waterproofing ability that can shield the roof’s membrane from water and moisture damage. You can also count on the liquid roof coating for its outstanding performance for a wide range of applications and uses. This product can be used at tears and seams as well as in sealing air conditioners and venting systems and anywhere else where rubberized coating is needed. https://youtube.com/e/ggLAUsiuI_o
This stuff works GREAT ! I live in an older mobile home that had a lot of leaks when I moved-in. I worked for two years to locate and fix them all. Now I simply go over all of the repaired places once a year just to be sure everything is OK. NO LEAKS FOR 4 YEARS NOW!!  Others here use "sno proof" or something that does not stop leaks. When I tell them about my success, they don't seem to want to pay the$ for this superior product. Too bad!. I used the tape in  repairing the leaks. https://www.youtube.com/watch?feature=youtube_gdata&v=ggLAUsiuI_o
There is a significant price difference when it comes to using foam insulation to insulate a new versus older home. Spraying insulation inside a newly constructed home is easier because the installation company can ensure the insulation will work effectively and design it for optimum defense against sound, heat transfer and utility costs. Installing spray foam in older homes that contain existing insulation can cost additional time and money -- it is not usually recommended as compared to weatherization or an energy aduit.

How Much For Spray Foam


For large jobs, professionals such as Dr. Energy Saver use two-part foam, which comes in larger containers. With 2-part spray foam, it's necessary to mix separate resin and catalyst compounds at the application nozzle. Combining these ingredients starts a chemical reaction that creates expanding foam. Contractors use small 2-part foam "kits" to air-seal an attic or to seal and insulate ductwork. To insulate an entire attic or wood-framed wall with spray foam, the resin and catalyst compounds are pumped to the application nozzle from 50-gallon drums in a specially equipped truck. http://www.youtube.com/v/ggLAUsiuI_o&feature=youtube_gdata

I live in Baton Rouge LA with a very old and drafty house. There is no blockages in the walls between the crawl space and attic. Lots of critters just come on in. I would like to used closed cell sprayed under house to warm up floors and block moisture. I would like to spray closed cell into attic, but am afraid of enclosing attic due to moisture build-up. Can I spray closed cell against the attic floor in same way as installing bats, thus leaving my venting the same as it always has been. Other ideas? Thanks.


This coating is also efficient with a coverage area reaching between 42 and 46 feet. And regardless of the weather, you can apply and use it in your roof to achieve the protection for it you need. Just as what you can read in RV rubber roof coating reviews, this product can work in all temperatures. Regardless it is hot or cold outside, you can easily apply and ensure of its adhesion on your recreational vehicle roof.
In the early days of insulating attics, people believed the insulation was a heat source. That’s not the case, as the insulation is actually a barrier between two areas of different temperatures. As for the “hot roof” theory, the unvented attic system could make the temperature of the roof go up a little, but this increase won’t cause damage to your shingles.
Although we are a small-town company, we can handle any size project or building. We have been blessed to work for residential homeowners as well as corporations like Bell Helicopter, Taco Bell, Tyson Foods, and even the Texas Rangers!  Our conservative Christian family values won’t let us give you anything less than an honest evaluation of the best product for your specific application. SprayFoam Texas installs the most energy efficient attic systems available anywhere. 
Silicone based coatings can be spray or roller-applied, and should utilize a medium-nap roller when rolled. These coatings are applied anywhere from 2 to 3.5 gallons per 100 square feet, depending on the substrate. Silicone has two major advantages over the other four types of coatings that should be considered when searching for the best roof coating: 1) it can resist ponding water for extended periods of time and 2) it can adhere to most substrates without a primer. Because of these two major advantages, silicone is the best roof coating that satisfies both quality and cost-effectiveness.
Spray foam is a very specialized packing material, often required for use in shipping valuable fragile items. Engineered packaging principles are designed to protect sculptures, vases, large fossils, lamp bases, busts, computers, furniture, chandeliers and other objects of unusual shape. By virtue of the liquid foam expanding by up to 30-60 times the volume of its liquid state, it efficiently protects almost any size, form and weight. http://youtube.com/watch?feature=youtube_gdata&v=ggLAUsiuI_o

This tropic heat actually is the cause that the steel structure, which most roofs in that part of the world are built on, expands and contracts all the time. By doing so, the sun-battered steel structure causes the roof tiles to dislodge and slowly creates small openings between the roof tiles, through which rain water can run into, creating leaks that can cause much damage to plastered ceilings and electric wiring.

I've seen this only once, and it was with closed cell foam, but I've heard of it happening with open cell foam, too. I don't know the details, but I've heard it could result from a bad batch of chemicals, improper mixing, or too high a temperature. Whatever the cause, it's not a good thing. The photo below shows how the spray foam pulled away from the studs. A little bit of uninsulated area like that adds up to a lot of heat loss/gain when the whole house has that problem, as it did here.

How Much Is Spray Foam Roof Insulation

×